If as I suspect fault is in another caravan on the site, if you returned to site likely now no fault apparent. Although clearly the site has outlets without RCD protection.
We are told an earth rod needs 300Ω or less to ensure it has a connection and will not dry out, but with a 30 mA RCD to ensure no more than 50 volt above true earth 50/0.030 = 1666Ω which you could likely get from a tent peg.
If a RCD has become insensitive i.e. faulty then it would not need that much of a fault to cause the earth to become live, with no RCD on a 16A supply you would need an earth loop impedance of 3Ω to ensure the MCB tripped. To get 3Ω you would need a TN supply which in UK is not permitted on most sites as the supplies are normally TN-C-S to the site, and only where a TN-S supply is guaranteed can you use a TN supply.
In UK the step down transformer has to have an earth rod better than 15Ω so even if site earth rod was zeroΩ you could still not guarantee it would trip.
So even on a UK site, we rely on the owner doing a test of all outlets to ensure the RCD works. In theory there is no point having a RCD in the caravan, as all sites should have a RCD on the supply anyway, however it is possible the site was laid out before the point when RCD's were required, my earliest version of BS7671 is 2004 when RCD's were required.
In UK there is no need to rush out and update installations when a new BS7671 is issued, in fact there is no legal requirement to follow it. However if you don't then if there is an accident then it can be used to show one did not take reasonable care.
So if a site was laid out in 1990 to 15th edition wiring regulations with ELCB-v fitted, there is nothing to say they must upgrade. As how one would today test an ELCB-v I really don't know? Today we use ELCB-c so modern test gear would not work with old units.
The old unit introduced a resistance into the earth and relied on no earth after the device, so if you connect the leg steadies to earth supply and wind them into the grass they would reduce the chance of a ELCB-v tripping, which is why their use was discontinued.
Problems with earthing is not only with caravan sites, I have found whole houses without an earth.
Because in Europe line and neutral may be swapped we really do need a plug in tester, with a loop test if possible, however since using an earth rod as long as the 500Ω light is on that's good enough.
One would also need a 16A to 13A adaptor to test before plugging in caravan. However with a ELCB-v the plug in tester would always show fail even if it was A1.
|
17/2/2019 at 4:27pm
Location: South Wales (UK) Outfit: Hobby + Swedish Tug
View Profile
Reply
Quote
|
Joined: 05/4/2007 Gold Member
Forum Posts: 373
Site Reviews Total: | 3 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
Quote: Originally posted by ericmark on 17/2/2019
If as I suspect fault is in another caravan on the site, if you returned to site likely now no fault apparent. Although clearly the site has outlets without RCD protection.
We are told an earth rod needs 300Ω or less to ensure it has a connection and will not dry out, but with a 30 mA RCD to ensure no more than 50 volt above true earth 50/0.030 = 1666Ω which you could likely get from a tent peg.
If a RCD has become insensitive i.e. faulty then it would not need that much of a fault to cause the earth to become live, with no RCD on a 16A supply you would need an earth loop impedance of 3Ω to ensure the MCB tripped. To get 3Ω you would need a TN supply which in UK is not permitted on most sites as the supplies are normally TN-C-S to the site, and only where a TN-S supply is guaranteed can you use a TN supply.
In UK the step down transformer has to have an earth rod better than 15Ω so even if site earth rod was zeroΩ you could still not guarantee it would trip.
So even on a UK site, we rely on the owner doing a test of all outlets to ensure the RCD works. In theory there is no point having a RCD in the caravan, as all sites should have a RCD on the supply anyway, however it is possible the site was laid out before the point when RCD's were required, my earliest version of BS7671 is 2004 when RCD's were required.
In UK there is no need to rush out and update installations when a new BS7671 is issued, in fact there is no legal requirement to follow it. However if you don't then if there is an accident then it can be used to show one did not take reasonable care.
So if a site was laid out in 1990 to 15th edition wiring regulations with ELCB-v fitted, there is nothing to say they must upgrade. As how one would today test an ELCB-v I really don't know? Today we use ELCB-c so modern test gear would not work with old units.
The old unit introduced a resistance into the earth and relied on no earth after the device, so if you connect the leg steadies to earth supply and wind them into the grass they would reduce the chance of a ELCB-v tripping, which is why their use was discontinued.
Problems with earthing is not only with caravan sites, I have found whole houses without an earth.
Because in Europe line and neutral may be swapped we really do need a plug in tester, with a loop test if possible, however since using an earth rod as long as the 500Ω light is on that's good enough.
One would also need a 16A to 13A adaptor to test before plugging in caravan. However with a ELCB-v the plug in tester would always show fail even if it was A1.
Luvved your L O N G reply but this was in Morocco and a different set of rules and regulations apply and if you can find them, then you are a better man than Gunga Din!
------------- According to Winnie the Pooh .... “Planning is what you do before you do it so that when you do it you don't get mixed up".
|
|
|
8343 Visitors online !
Free UKCampsite.co.uk Window Sticker - Recommend to Friend - Add a Missing Campsite
[Message Forums]
[Caravan Sites & Camping]
[Company Listings]
[Features / Advice]
[Virtual Brochure]
[Shop!]
[Reception]
[Competitions]
[Caravans & Motorhomes For Sale]
[Event Diary]
[Contact Us]
[Tent Reviews]
Please note we are not responsible for the content of external sites & any reviews represent the author's personal view only. Please report any error here. You may view our privacy and cookie policy and terms and conditions here. All copyrights & other intellectual property rights in the design and content of this web site are reserved to the UKCampsite.co.uk © 1999 - 2024
|
Advertisement
|
|
|