I can only speak for the specifications in the U.K. but I suspect that the majority of RCDs are manufactured to the same tolerances.
The UK requirements for RCDs is that they should operate between 50% and 100% of their rated tripping current,most 30 mA RCDs operate at between 18 mA and 23 mA.You will see that if a 10 mA RCD is manufactured to the same standard its tripping current could possibly be as low as 5 mA,I think this would be far too low for the harsh conditions experienced on a campsite and would lead to nuisance tripping.A 30 mA RCD is considered to be the safest and least troublesome for personal protection.
To ensure discrimination a factor of three is required for the upstream RCD so a 30 mA RCD would need a 90mA RCD(a 100mA unit is normally used) upstream and it would also need to be a type C time delayed.It doesn't have to be time delayed but if you want to guarantee discrimination it needs to be.
If all your pitches have individual 30 mA RCDs then under the regs in the UK a 100mA time delayed unit is acceptable upstream,this then copes with the discrimination problem and also the combined earth leakage situation caused by capacitance and imperfect insulation from the total no of units connected.
As all the downstream RCDs offer the required personal protection then the function of the upstream RCD is mainly equipment protection, fire prevention being the primary one, but it will still offer a reduced level of shock protection.
The above applies to the UK it may be different for mainland Europe
Saxo1
|
20/8/2012 at 7:33am
Location: Denmark Outfit: Campsite owner
View Profile
Reply
Quote
|
Joined: 24/8/2007 Standard Member
Forum Posts: 59
Site Reviews Total: | 0 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
Quote: Originally posted by saxo1 on 19/8/2012
I can only speak for the specifications in the U.K. but I suspect that the majority of RCDs are manufactured to the same tolerances. The UK requirements for RCDs is that they should operate between 50% and 100% of their rated tripping current,most 30 mA RCDs operate at between 18 mA and 23 mA.You will see that if a 10 mA RCD is manufactured to the same standard its tripping current could possibly be as low as 5 mA,I think this would be far too low for the harsh conditions experienced on a campsite and would lead to nuisance tripping.A 30 mA RCD is considered to be the safest and least troublesome for personal protection. To ensure discrimination a factor of three is required for the upstream RCD so a 30 mA RCD would need a 90mA RCD(a 100mA unit is normally used) upstream and it would also need to be a type C time delayed.It doesn't have to be time delayed but if you want to guarantee discrimination it needs to be. If all your pitches have individual 30 mA RCDs then under the regs in the UK a 100mA time delayed unit is acceptable upstream,this then copes with the discrimination problem and also the combined earth leakage situation caused by capacitance and imperfect insulation from the total no of units connected. As all the downstream RCDs offer the required personal protection then the function of the upstream RCD is mainly equipment protection, fire prevention being the primary one, but it will still offer a reduced level of shock protection. The above applies to the UK it may be different for mainland Europe Saxo1
Thanks very much for going to the trouble of writing that saxo - in particular the info about rating and overlapping ranges sheds light.
I appreciate it!
Thanks
Jon
|
20/8/2012 at 10:45pm
Location: Wiltshire Outfit: Outwell Montana 6P
View Profile
Reply
Quote
|
Joined: 14/5/2008 Silver Member
Forum Posts: 111
Site Reviews Total: | 0 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
Hi Jon,
Just read through your thread and was wondering what the intended purpose of the central (feeding 20 points) 30mA RCD was?
Given that each socket is individually protected by its own RCD (as required by the latest regs) the upstream 30mA RCD serves no real purpose and is indeed likely to suffer from nuisance trips given the lack of discrimination as discussed.
The wiring between your central distribution point and each pitch outlet should be installed and physically protected (depth or height below/above ground, mechanical protection, etc) such that no additional protection is required to guard against electrocution. As Saxo suggests, a time-delayed 100mA (possibly even higher as that is only 5mA leakage per pitch) would be your best belt-and-braces option in the distribution point. Overcurrent protection is still required to protect the wiring to each outlet but that is a separate issue.
It should be borne in mind that so-called nuisance trips could themselves be a safety hazard should an unsuspecting camper be plunged into darkness as a result of the action of another camper e.g. from trips/falls, scalding, etc and so mitigation of this risk should have been designed in at the outset. It is on this basis that, for redential properties, 'whole-house' RCDs are no longer permitted by the regs because more people were being killed/injured from falls down stairways in the dark than would otherwise be caused by fixed wiring faults that the RCD was intended to protect!
Hopefully this goes without saying but you should seek the advice of a qualified electrician rather than taking anything said here as necessarily valid. Aside from anything there are many other factors, such as the type of supply and distribution earthing, that will also have an influence over exactly what protection is required.
Mathew
Post last edited on 20/08/2012 23:25:15
|
21/8/2012 at 8:37am
Location: Denmark Outfit: Campsite owner
View Profile
Reply
Quote
|
Joined: 24/8/2007 Standard Member
Forum Posts: 59
Site Reviews Total: | 0 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
Quote: Originally posted by mjnewton on 20/8/2012Hi Jon,Just read through your thread and was wondering what the intended purpose of the central (feeding 20 points) 30mA RCD was?
Given that each socket is individually protected by its own RCD (as required by the latest regs) the upstream 30mA RCD serves no real purpose and is indeed likely to suffer from nuisance trips given the lack of discrimination as discussed.
The wiring between your central distribution point and each pitch outlet should be installed and physically protected (depth or height below/above ground, mechanical protection, etc) such that no additional protection is required to guard against electrocution. As Saxo suggests, a time-delayed 100mA (possibly even higher as that is only 5mA leakage per pitch) would be your best belt-and-braces option in the distribution point. Overcurrent protection is still required to protect the wiring to each outlet but that is a separate issue.
It should be borne in mind that so-called nuisance trips could themselves be a safety hazard should an unsuspecting camper be plunged into darkness as a result of the action of another camper e.g. from trips/falls, scalding, etc and so mitigation of this risk should have been designed in at the outset. It is on this basis that, for redential properties, 'whole-house' RCDs are no longer permitted by the regs because more people were being killed/injured from falls down stairways in the dark than would otherwise be caused by fixed wiring faults that the RCD was intended to protect!
Hopefully this goes without saying but you should seek the advice of a qualified electrician rather than taking anything said here as necessarily valid. Aside from anything there are many other factors, such as the type of supply and distribution earthing, that will also have an influence over exactly what protection is required.
Mathew
Post last edited on 20/08/2012 23:25:15
As far as I understand it the RCD at the pitch may not protect the operator digging or working upstream. Either way it is standard design and as far as I am aware fully mandatory.
Campsite regs also require us to have adequate lighting and we have illumination throughout the campsite.
We do not suffer many nuisance trips, I have said in previous posts that almost all of our trips are repeatable and associated with one item of equipment which can then be demonstrated to be able to trip a 30mA RCD when it is the only thing on the circuit ( I mentioned we unplug everyone as part of our investigative procedure ). So despite repeated theoretical claims the observed behaviour is that actually a 30mA RCD can serve a modest number of campers without nuisance trips.
You are right about qualified advice but I have read professional forums on the matter and you might be surprised to know that many professionals seem to get puzzled on series RCD issues and often ask each other questions of this nature.
I would of course take any information offered by Mojo and Saxo and pass it by a professional but I have to say that so far I have been very impressed by the knowledge displayed by these two. Advice is not dangerous if it is subsequently verfied and confirmed by professionals and I have not necessarily obtained the same clarity and illumination talking to professionals. I tend to find I get best results from pros when I am armed with a fairly full understanding of the issues myself.
I assure you that standards/regs that determine what I can or cannot do in Denmark are very high and anything I do is subject to regular inspection.
Thanks Jon
PS As far as I have been able to assertain I am most likely not allowed 100mA upstream, actually seems that the English regs are a bit loose here as 100mA is commonly quoted in the online sources I have consulted as being the agreed lethal threshold ( varies of course )
I noted my comments on nuisance trips dont properly take into account that the other users on the same leg do actually experienced a nuisance trip because it would not have happend to them if a single RCD so your comment has validity as far as the others are concerned. A valid trip can still be a nuisance trip - depends not only on the event but on the collateral consequence, I am confusing the issue by failing to differentiate between nuisance trip and shall we say "justified trip".
Post last edited on 21/08/2012 09:56:48
Post last edited on 21/08/2012 10:02:40
Post last edited on 21/08/2012 10:05:00
|
|
|
6261 Visitors online !
Free UKCampsite.co.uk Window Sticker - Recommend to Friend - Add a Missing Campsite
[Message Forums]
[Caravan Sites & Camping]
[Company Listings]
[Features / Advice]
[Virtual Brochure]
[Shop!]
[Reception]
[Competitions]
[Caravans & Motorhomes For Sale]
[Event Diary]
[Contact Us]
[Tent Reviews]
Please note we are not responsible for the content of external sites & any reviews represent the author's personal view only. Please report any error here. You may view our privacy and cookie policy and terms and conditions here. All copyrights & other intellectual property rights in the design and content of this web site are reserved to the UKCampsite.co.uk © 1999 - 2024
|
Advertisement
|
|
|