Advertisement
Message Forums |
|
Topic: Extending the EHU cable
|
Page: 1 2 3
|
13/4/2012 at 10:57pm
Location: Surrey Outfit: Peugeot Boxer Utah + Lunar Ariva
View Profile
Reply
Quote
|
Joined: 23/1/2011 Diamond Member
Forum Posts: 1839
Site Reviews Total: | 4 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
It is not uncommon to see 2 EHU cables put together if the hook up point is a longer way away from their unit. I have seen many wardens joining the campers & the camps EHU together. We have had to have the same ourselves twice. Once via the Camplet TT we had a couple of years ago. The first though was our VW camper van. One was on Hereford CCC site & the other was California Cliffs CCC site. We have 2 x 25 met. cables as we never let them go when being sold only the Camplet time as we already had 2 did not need the third one.
I can see the the neatness part and possibly the safety side so it never gets pulled apart by anyone or anything driving over it.
But what does it do in laymans terms if both the cables are the same except for colour as one is blue the other is orange. Because this is a post that has got be more baffled by its answers than anything I have read before. So it will and is teaching me nothing what so ever to add to my little black book I write all help inside and carry with us camping.
We use only electric, a fridge,kettle standard one from home,Remoska, Microwave, & Halogen cooker. Plus fan heater 1000w & 2000w. We are very careful not to have any 2 of the big things on. So it is fridge-standard + one of the others+ lights possibly. Have not put in extra plugholes so we never make the mistake. So we only have 2 plug holes and the main one is on top where the kettle is. The other behind the t.cloth so not used unless using the table to cook on, making the higher one for the kettle left unplugged always.
All I can see from this is what is going through my brain. it seems to be if one cable is short the other long. the v changes. If both are joined together even if the same type of cable, over the length the v. changes. or is this completely wrong & senseless. Because that is what a layperson is getting and not understanding. Can we use 2 cables if necessary or not? If we can, we can also neaten for safety sake by the cover.
Over to you. My black book is waiting. Just make it PLAIN speaking to a NON eletrical person/persons
------------- Chrissie
Be Strong-Think positive.
|
14/4/2012 at 6:10am
Location: Argyll Scotland Outfit: 1997 Bailey Ranger 470 4
View Profile
Reply
Quote
|
Joined: 28/12/2002 Diamond Member
Forum Posts: 8833
Site Reviews Total: | 5 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
Chrissie, I take it that you are asking what the red junction box is for?
<<<I can see the the neatness part and possibly the safety side so it never gets pulled apart by anyone or anything driving over it.
But what does it do in laymans terms if both the cables are the same except for colour as one is blue the other is orange. Because this is a post that has got be more baffled by its answers than anything I have read before. So it will and is teaching me nothing what so ever to add to my little black book I write all help inside and carry with us camping.>>>
Both the plug and the socket of an EHU Cable is set into the caravan/FC and into the sites EHU box, at such an angle as to make these connections waterproof.
However if you join 2 EHU cables together, because they are lying on the ground, they are not waterproof. They are lying on their side, in a position that they are not meant to be used in and therefore you should have that joint inside some sort of waterproof box. It is neither for neatness nor to stop it getting pulled apart. It is purely to keep water out of the plug and socket of 2 joined EHU Cables while they are lying on the ground in wet weather.
------------- Lobey.
|
14/4/2012 at 9:45am
Location: Yeadon Leeds! Outfit: Swift Challenger & Defender 110SW
View Profile
Reply
Quote
|
Joined: 27/6/2005 Diamond Member
Forum Posts: 3331
Site Reviews Total: | 10 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
I think the best I have seen was a site last year, long cable, draped accross the "roadway" not a made up surface, but was the main thorough fair for traffic, the plug join wrapped in a carrier bag, and buried because it was 1/2 way across the "road"
with regard to the voltage drop for the OP, seeing as the CPAP in question has a voltage input of 100-240V, leads me to the conclusion of a switch mode power supply, which, as long as the voltage is above its minimum, couldn't give a damn about a few volts here or there.
Im not exactly sure how much I'd trust one of those rugbyball things, there's no official IP rating on them, so you have no idea of the additional protection they offer.
|
14/4/2012 at 10:42am
Location: Shropshire Outfit: Toyota Granvia (Wellhouse)
View Profile
Reply
Quote
|
Joined: 30/9/2007 Diamond Member
Forum Posts: 3872
Site Reviews Total: | 19 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
Quote: Originally posted by ianclose on 13/4/2012
Quote: Originally posted by pepe63 on 13/4/2012
GoOutdoors sell something similar:
http://www.ukcampsite.co.uk/redirect.asp?redir=http://www.ukcampsite.co.uk/redirect.asp?redir=http://www.gooutdoors.co.uk/electrosafe-p150010
...although still best part of a fiver on top,if you want it delivered...
Just ordered that one myself. Free delivery until Sunday as well.
I'm glad I just happend to check back..!
(..'twas definately a fiver when I originally posted the link..)
To Lobey..
I bet with all this "voltage drop".."I can't see the point".."just change your plug & socket" malarky,you're beginning to wish you hadn't asked!
For those concerned with posssible voltage drops(..what with kettles taking longer to boil!? ),then I suggest you use gas or insist on a pitch closer to the socket!...
..and for those who just "can't see the point"..well...then just don't buy one..!
|
14/4/2012 at 9:56pm
Location: Surrey Outfit: Peugeot Boxer Utah + Lunar Ariva
View Profile
Reply
Quote
|
Joined: 23/1/2011 Diamond Member
Forum Posts: 1839
Site Reviews Total: | 4 |
|
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
Site Reviews 2018: | 0 |
|
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
Site Nights 2018: | 0 |
|
Lobby
However if you join 2 EHU cables together, because they are lying on the ground, they are not waterproof. They are lying on their side, in a position that they are not meant to be used in and therefore you should have that joint inside some sort of waterproof box. It is neither for neatness nor to stop it getting pulled apart. It is purely to keep water out of the plug and socket of 2 joined EHU Cables while they are lying on the ground in wet weather.
Now I know they should be covered as the only way we had seen 2 x 25 met leads joined have been just left on the grass or going acros the sites road under a rubber tubing so that cars etc can driver over it.
I always connect the EHU and I unwind it all and do not let the cable over lap each other, Just do it like a sssss with a couple of coloured rags tied on it if it goes across somebodies shortcut. As it had at West Runton. Someone got so close to our fc they trippe over the cable and slammed against my bedside whilst I was laying down having a rest pm.Frightened the willies out of me with the almighty thump he made on the side. Checked for damage, thankfully none on the fc but his toes hurt. Then he should not of been that close should he. Anyway I put markers on it to show it is there so nobody hurts themselves, as sometimes it has to go nearly a full 25mt away.
We have a small one that is only like the standard 3 pin house plug and connection to the fc. My brother in law froze his fridge down before he left home and kept it like freezer all his hols. But we would like a 10 mt one as many times the long one is just far too long when it can be a behind the fc connection. I have actually had to unwind half way round the fc back n fro before now.So sense to have a shorter one.
------------- Chrissie
Be Strong-Think positive.
|
|
|
6246 Visitors online !
Free UKCampsite.co.uk Window Sticker - Recommend to Friend - Add a Missing Campsite
[Message Forums]
[Caravan Sites & Camping]
[Company Listings]
[Features / Advice]
[Virtual Brochure]
[Shop!]
[Reception]
[Competitions]
[Caravans & Motorhomes For Sale]
[Event Diary]
[Contact Us]
[Tent Reviews]
Please note we are not responsible for the content of external sites & any reviews represent the author's personal view only. Please report any error here. You may view our privacy and cookie policy and terms and conditions here. All copyrights & other intellectual property rights in the design and content of this web site are reserved to the UKCampsite.co.uk © 1999 - 2024
|
Advertisement
|
|
|