Can't say for sure, but I think the blue BS4343 outlet plug is the same on the continent. (It's not BS4343 now - it has a European number which I can't remember for the life of me!) - you should be able to confirm this quite easily, either thru the net or from a reputable retailer. If this is the case, you're good to go!
What I will say is that it's essential your EHU trips are DOUBLE POLE - ie. breaks live and neutral. This is because 220v European supplies are distributed 110v on the live, 110v on the neutral as opposed to UK 230v on the live, 0v on the neutral. So by having double pole isolation, you won't get a nasty tickle! And make sure your RCD works by giving it a functional check - ie press the TEST or 'T' button when connected to a supply - it MUST trip out. If it does not, check there is a supply to it and try it again. If it still doesn't trip, it is defective and MUST be replaced.