That is an RCBO, earth leakage trip ,you have a faulty kettle or fridge or perhaps a fault on the wiring to those appliance try each one separately to determine which one is causing it.
It has nothing to do with the wattage, the figure of 0.o3A refers to the fault current rating to trip the breaker.
saxo1
|
02/4/2024 at 6:27pm
Location: None Entered Outfit: None Entered
View Profile
Reply
Quote
|
Joined: 29/10/2005 Diamond Member 
Forum Posts: 4490
Site Reviews Total: | 0 |
|
Site Reviews 2025: | 0 |
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
|
Site Nights 2025: | 0 |
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
|
A 6A supply should be more than adequate to run a fridge and a low wattage travel kettle if that is all you have on at the same time!
Saxo1
|
02/4/2024 at 7:38pm
Location: Outfit:
View Profile
Reply
Quote
|
Joined: 11/8/2016 Diamond Member 
Forum Posts: 3150
Site Reviews Total: | 3 |
|
Site Reviews 2025: | 0 |
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 3 |
|
Site Nights 2025: | 0 |
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 15 |
|
Quote: Originally posted by saxo1 on 02/4/2024
A 6A supply should be more than adequate to run a fridge and a low wattage travel kettle if that is all you have on at the same time!
Saxo1
dont forget the battery charger will be on too, which would take it over the 1000 watts for 6 amps
|
02/4/2024 at 10:36pm
Location: Devizes Wiltshire Outfit: MWB2BVW2BCrafter2
View Profile
Reply
Quote
|
Joined: 19/6/2009 Diamond Member 
Forum Posts: 9708 Tent Reviews: 6
Site Reviews Total: | 57 |
|
Site Reviews 2025: | 0 |
Site Reviews 2024: | 10 |
Site Reviews 2023: | 9 |
Site Reviews 2022: | 8 |
Site Reviews 2021: | 9 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
|
Site Nights 2025: | 0 |
Site Nights 2024: | 49 |
Site Nights 2023: | 47 |
Site Nights 2022: | 46 |
Site Nights 2021: | 34 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
|
Quote: Originally posted by 664DaveS on 02/4/2024
That is low for a UK hookup!
Not uncommon though, as I have to stay away from certain sites as they only have 6A EHU, such as Tuckers Grave Inn near Bath, a nice pub with lots of ciders and free entertainment. They are supposed to be upgrading their supply to 10A, however, Covid delayed it, and it would cost quite a bit to upgrade. The local V-dub club had a camp out there last weekend, however, I was not able to join them as I was away camping.
DK
------------- Apple The Campervan - A Van For Work, Rest & Play!
- 2025: 19/71 inc. Scotland
- 2024: 10/49 inc. FR & NL
- 2023: 9/47 inc. FR
- 2022: 8/46
- 2021: 9/34
* Treat life events like a dog: if you can't eat it, play with it or hump it, p1$$ on it and walk away!
|
03/4/2024 at 11:26am
Location: nr Derby Outfit: Phoenix 440+
View Profile
Reply
Quote
|
Joined: 09/7/2008 Diamond Member 
Forum Posts: 3781
Site Reviews Total: | 26 |
|
Site Reviews 2025: | 0 |
Site Reviews 2024: | 3 |
Site Reviews 2023: | 2 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
|
Site Nights 2025: | 0 |
Site Nights 2024: | 6 |
Site Nights 2023: | 6 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
|
6 amps should be enough to run the fridge and the kettle; i don't think the charger would be working all the time as the battery should be fully charged ( I'm not an electrician!). We have stayed on sites with 6Amp supply often and are always conscious never to have two 'heating' appliances on together and have never had a problem apart from once when the kettle was the culprit and needed to be replaced.
------------- Grahame
|
03/4/2024 at 11:29am
Location: None Entered Outfit: None Entered
View Profile
Reply
Quote
|
Joined: 29/10/2005 Diamond Member 
Forum Posts: 4490
Site Reviews Total: | 0 |
|
Site Reviews 2025: | 0 |
Site Reviews 2024: | 0 |
Site Reviews 2023: | 0 |
Site Reviews 2022: | 0 |
Site Reviews 2021: | 0 |
Site Reviews 2020: | 0 |
Site Reviews 2019: | 0 |
|
Site Nights 2025: | 0 |
Site Nights 2024: | 0 |
Site Nights 2023: | 0 |
Site Nights 2022: | 0 |
Site Nights 2021: | 0 |
Site Nights 2020: | 0 |
Site Nights 2019: | 0 |
|
Quote: Originally posted by marg6 on 02/4/2024
Quote: Originally posted by saxo1 on 02/4/2024
A 6A supply should be more than adequate to run a fridge and a low wattage travel kettle if that is all you have on at the same time!
Saxo1
dont forget the battery charger will be on too, which would take it over the 1000 watts for 6 amps
1000W at 240 Volts is only app 4.17 amps.
A 6 amp RCBO won't trip a just over 6 amps there is a considerable margin over 6 amps before they trip.
saxo1
|
|